OPCUA connection lifetime8
Avatar
Pham Ngoc Song Ha
Member
Members
Forum Posts: 21
Member Since:
11/15/2021
sp_UserOfflineSmall Offline
1
03/30/2022 - 04:16
sp_Permalink sp_Print

Hi,

I have a PLC (Server) connected to my PC (Client) via OPC UA protocol. When I check the KeepAliveEventArgs.status from KeepAliveEventHandler, I see the connection expires after 2 or 3 days so I think there is a life time in the session. Is there any way to make it permanent?

thank you in advance.

Avatar
Randy Armstrong
Admin
Forum Posts: 1564
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
2
03/30/2022 - 05:54
sp_Permalink sp_Print

Session should never expire as long as they are active.

Sounds like a bug in the client or server.

What error codes do you see.

Avatar
Randy Armstrong
Admin
Forum Posts: 1564
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
3
03/30/2022 - 05:56
sp_Permalink sp_Print

Specifically, this sounds like it could be a sequence number wrap-around error. Are you sending a lot of messages?

Avatar
Pham Ngoc Song Ha
Member
Members
Forum Posts: 21
Member Since:
11/15/2021
sp_UserOfflineSmall Offline
4
03/30/2022 - 07:53
sp_Permalink sp_Print

thank you for your quick response

There is no error code. I was checking the property Session.KeepAliveStopped in KeepAliveEventHandler and at some point (perhaps after 3 days), the flag showed false.

The PLC just sent the live signal to the PC. There was no message transferred in this case. What do you mean by sequence number wrap-around error?

Moreover, I find the Opc.Ua.ApplicationConfiguration.ClientConfiguration.DefaultSessionTimeout property. Could it define the life time of the session?

Avatar
Randy Armstrong
Admin
Forum Posts: 1564
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
5
03/30/2022 - 09:56
sp_Permalink sp_Print

DefaultSessionTimeout only affects the timeout for idle sessions. If you are sending heartbeats the session will not timeout.

SequenceNumber wrapping error is a low level protocol error which you would need WireShark to detect (WireShark has an OPC UA plugin).

What else are you doing in those 3 days? Can you summarize the interactions between your client and the PLC in those 3 days?

Avatar
Pham Ngoc Song Ha
Member
Members
Forum Posts: 21
Member Since:
11/15/2021
sp_UserOfflineSmall Offline
6
03/31/2022 - 01:41
sp_Permalink sp_Print

Hi,

do you have any document explaining SequenceNumber wrapping error?

according to your explanation, I think of network interruption in this case, because if someone restarted the PLC, my logic in it should reinitiate the connection again. However if the OPC UA's connection lost, the PLC could not recognize by itself. Is there any flag variable in PLC site, which allows me to observe the connection state? 

I did implement this in KeepAliveEventHandler for PC's side:

while ServiceResult.IsGood(Session.KeepAliveEventArgs.Status)

      Session.reconnect

      if timer > 5 Min

           break

      end if

end while

However it seems the reconnect method didn't work, or the reconnection effort was timeout. Does the reconnect method work based on this instruction: https://reference.opcfoundatio.....Part4/6.7/ ?

Avatar
Randy Armstrong
Admin
Forum Posts: 1564
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
7
03/31/2022 - 03:46
sp_Permalink sp_Print

OK - I was assuming there were no network interruptions or PLC restarts that would explain the dropped session. If the network is interrupted then the KeepAliveEvent allows you to trigger the recovery logic in your client.

Only part of that recovery logic is implemented in the NETStandard codebase. Do you have recovery logic in your Client?

Avatar
Pham Ngoc Song Ha
Member
Members
Forum Posts: 21
Member Since:
11/15/2021
sp_UserOfflineSmall Offline
8
03/31/2022 - 09:13
sp_Permalink sp_Print

I call session.reconnect for recovery. Do you think that is not enough?

Is there anything I have to do with live signal from PLC? Till now I only use it to check the Session.KeepAliveEventArgs.Status periodically.

Avatar
Randy Armstrong
Admin
Forum Posts: 1564
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
9
03/31/2022 - 12:04
sp_Permalink sp_Print

You need to ask on the the GitHub project. I am not sure what the Reconnect does.

If you can create a new Session after Reconnect fails it sounds like a bug in Reconnect.

Avatar
Pham Ngoc Song Ha
Member
Members
Forum Posts: 21
Member Since:
11/15/2021
sp_UserOfflineSmall Offline
10
04/18/2022 - 06:26
sp_Permalink sp_Print sp_EditHistory

Hi,

after many experiments, I realize that the session is not expired, the connection is still there. The subscription could be the problem. I read the documentation and find out that there is lifetimecount property which could be relevant to the phenomena. The variable I monitor in PLC changes very little. Sometime it stays the same the whole day.

In the documentation 5.13.1.1 of OPC UA Online Reference it is said:

After creation of the Subscription, the Server starts the publishing timer and restarts it whenever it expires. If the timer expires the number of times defined for the Subscription lifetime without having received a Subscription Service request from the Client, the Subscription assumes that the Client is no longer present, and terminates.

As far as I can understand, I have to let the client send publish request to the server to reset the timer or raise the lifetime of the subscription.

Can I change the lifetime of the subscription by setting the variable MinLifetimeInterval? Is it in second or millisecond?

How can I perform the publish request to the server? I can't see any variable for that.

Avatar
Randy Armstrong
Admin
Forum Posts: 1564
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
11
04/18/2022 - 09:03
sp_Permalink sp_Print

The Session/Subscription objects on the client side send publishes automatically.

Your subscriptions should not be timing out due to lifetime.

You should get a keep alive message for each subscription.

Avatar
Pham Ngoc Song Ha
Member
Members
Forum Posts: 21
Member Since:
11/15/2021
sp_UserOfflineSmall Offline
12
04/18/2022 - 09:32
sp_Permalink sp_Print

I am using UA .NET stack to code the client.

You mean the keepalive event is from subscription, not from session? It sounds weird because the event is from the class opc.ua.client.session

Do you think if there is another reason to make a subscription expire in a session? I have found this topic and it shares similar problem.

https://opcfoundation.org/foru.....-or-event/

Avatar
Randy Armstrong
Admin
Forum Posts: 1564
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
13
04/18/2022 - 12:15
sp_Permalink sp_Print

The term keep alive is overloaded.

Each subscription returns and empty notification each time the keep alive expires (expressed as multiple of the publishing interval).

The subscription or session should have a event that allows you get notified when these messages arrive.

As long as the subscription keep alives come the subscription lifetime will not expire.

Separately the session has a timeout that will never happen as long as subscription keep alives are being received.

Lastly, the Session class has a watchdog timer that pings the server periodically and raises a client side event of the server does not respond. This also has the effect of ensuring the Session does not expire.

Avatar
Pham Ngoc Song Ha
Member
Members
Forum Posts: 21
Member Since:
11/15/2021
sp_UserOfflineSmall Offline
14
04/19/2022 - 04:57
sp_Permalink sp_Print

I have done an experiment and find out a very weird behavior. In this experiment, there are 2 subscription. The first one has one monitored item and it changes once. The second one has 5 monitored items and they don't change. I let the live signals of subscriptions printed and observe.

The first subscription seems to work normally. The live signals come each 10 seconds adequately.

The second subscription has kind of phenomenon. After 30 minute, some of its live signals start missing gradually. The live signals stop coming after 3 hour.

 

I have also done this experiment on 2 different PLCs and the phenomenon happened on both of them.

Avatar
Randy Armstrong
Admin
Forum Posts: 1564
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
15
04/19/2022 - 09:03
sp_Permalink sp_Print

What are the values if the revised parameters.

On the Subscription they are:

CurrentPublishingInterval

CurrentKeepAliveCount

CurrentLifetimeCount

Monitor these values:

PublishTime

LastNotificationTime

SequenceNumber

NotificationCount

Avatar
Pham Ngoc Song Ha
Member
Members
Forum Posts: 21
Member Since:
11/15/2021
sp_UserOfflineSmall Offline
16
04/20/2022 - 01:00
sp_Permalink sp_Print

Subscription parameter

CurrentPublishingInterval : 1s

CurrentKeepAliveCount : 10

CurrentLifetimeCount : 300 but LifetimeCount is 1000 (should they be the same?)

Monitor these values

PublishTime : 1/2/2012 12:49:11 AM (current clock in PLC)

LastNotificationTime : 2 hours sooner comparing with current time

NotificationCount : 1

SequenceNumber of the Subscription with 1 monitored item is 5

SequenceNumber of the Subscription with 5 monitored items is 2

Avatar
Randy Armstrong
Admin
Forum Posts: 1564
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
17
04/20/2022 - 01:48
sp_Permalink sp_Print

LifetimeCount can be reduced by the server. Your subscriptions expire after 300s of inactivity.

If everything is working correctly:

For both subscriptions you should see the PublishTime change every 10s.

That said, a bad clock on the PLC could be the source of your issues. Why is it so out of synch?

Avatar
Pham Ngoc Song Ha
Member
Members
Forum Posts: 21
Member Since:
11/15/2021
sp_UserOfflineSmall Offline
18
04/20/2022 - 03:09
sp_Permalink sp_Print

PublishTime change every 10s. This one is correct because I receive live signal from each subscription every 10s.

Inactivity of subscription here means no live signal, doesn't it? From what I have observe, if the subscription is created but the PLC tag doesn't change from the beginning, the live signals become weaker from time to time (not 10s anymore but somewhat 5min).

Is there anyway to make the LifetimeCount from the Server fix? 

 

I am gonna check how to change the clock in the PLC.

Avatar
Randy Armstrong
Admin
Forum Posts: 1564
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
19
04/20/2022 - 07:36
sp_Permalink sp_Print

The Session class is constantly sending PublishRequests which will ensure the Subscription is kept alive.

I was looking to confirm that this process is taking place.

SequenceNumber and NotificationCount should only change if the data changes.

Avatar
Pham Ngoc Song Ha
Member
Members
Forum Posts: 21
Member Since:
11/15/2021
sp_UserOfflineSmall Offline
20
04/26/2022 - 00:43
sp_Permalink sp_Print

Hi,

I have logged the publish error event and I have this record, which shows the behavior of the connection when it hits it lifetime limit.

- First the PLC sends all of the value of the subscribed tag. Although none of them is changed.

- Then there are publish errors:

26.04.22,02:42:41.2,INFO; Publish Error in Session: ns=1;i=3951517821; Statuscode: BadMessageNotAvailable
26.04.22,02:42:41.2,INFO; Publish Error in Session: ns=1;i=3951517821; Statuscode: BadConnectionClosed
26.04.22,02:42:41.2,INFO; Publish Error in Session: ns=1;i=3951517821; Statuscode: BadConnectionClosed

26.04.22,02:43:08.2,INFO; Publish Error in Session: ns=1;i=3951517821; Statuscode: BadSecureChannelClosed
26.04.22,02:43:10.8,INFO; Publish Error in Session: ns=1;i=3951517821; Statuscode: BadSecureChannelClosed

26.04.22,02:43:33.7,INFO; Publish Error in Session: ns=1;i=3951517821; Statuscode: BadSecureChannelClosed
26.04.22,02:43:36.3,INFO; Publish Error in Session: ns=1;i=3951517821; Statuscode: BadSecureChannelClosed

- After 3 times of the reports above, there is time out in session and the session is closed.

26.04.22,02:47:07.7,INFO;OPC_UA connection ends; SessionNr: ns=1;i=3951517821; Message: Reconnect timeout
26.04.22,02:47:07.8,INFO; Publish Error in Session: ns=1;i=3951517821; Statuscode: BadSessionClosed
26.04.22,02:47:07.8,INFO; Publish Error in Session: ns=1;i=3951517821; Statuscode: BadSessionClosed