It is possible it is related to server design: a server that did an update and waited for the next scan to check that the write was successful would introduce delays based on the scan frequency. If this is configurable you may be able to lower it.
It could be an implementation problem with the UA server. You could confirm it is specific to the UA server if you have another way to write to the PLC, such as a engineering tool provided by the PLC vendor.
I would also test by subscribing to the data point with a SamplingInterval and PublishingInterval of 0 or the lowest possible value. See how long it takes to get an update after sending the write. If the update arrives before the write response then that is evidence that the server is likely waiting for confirmation before returning a response.