Hello,

With reference to Part 13: Aggregates OPC UA Specifications I have the following questions

Section A.1.2 Example Aggregate data – Historian 2 has the following configuration

Stepped Attribute = False. Therefore SlopedInterpolation is used between data points.

UseSlopedExtrapolation = False. Therefore SteppedExtrapolation is used at end boundary conditions

 

Examining the Interpolative data in section A.2.2 for Historian2 , The last aggregate interval has used sloped extrapolation and computed the result instead of steped extrapolation( deviation from what is configured)

Could you please justify how the last aggregate interval has computed?

12:01:35.000 102.500 UncertainDataSubNormal, Interpolated
Avatar
Rod Stein
Canada
Member
Members
Forum Posts: 27
Member Since:
04/01/2014
sp_UserOfflineSmall Offline
2
02/18/2016 - 14:32
sp_Permalink sp_Print

You are correct to question the value because it is incorrect in table A.2.2 for Historian2 (UA spec 1.03).  The value should be 90 based on the previous Raw value and the UseSlopedExtrapolation being set to False.  The examples for Historan1 and Historian3 have the correct value.  This is an error and I will enter an issue at the OPC Foundation.

Rod Stein               Manager of Technology Matrikon OPC               http://www.matrikonopc.com

Avatar
Rod Stein
Canada
Member
Members
Forum Posts: 27
Member Since:
04/01/2014
sp_UserOfflineSmall Offline
3
02/18/2016 - 14:46
sp_Permalink sp_Print sp_EditHistory

Rod Stein               Manager of Technology Matrikon OPC               http://www.matrikonopc.com