sp_Feed sp_PrintTopic sp_TopicIcon
Usage of BAD OPCQualityCode
Avatar
Murali Janakiraman
New Member
Members
Forum Posts: 2
Member Since:
10/22/2020
sp_UserOfflineSmall Offline
1
02/10/2021 - 17:55
sp_Permalink sp_Print

Hi,

We use OPC quality Code of value BAD to indicate that the measurements value they represent are BAD. This information useful to the client though they are BAD and does not represent miscommunication or something. 

However, we noted that the OPC UA clients such as OPCExpert or Integration Objects OPC UA Client, show values set to OPCQualityCode BAD as null and not update the timestamp until the state changes GOOD or UNCERTAIN. Based on this behavior, we are not clear whether this is a defect in these clients or the OPC protocol allows such behavior/freedom to client implementations. If it is the later we need to rethink how we represent the BAD quality values though they are informational to the users. 

Thanks for your feedback and time,

 

Murali

Avatar
Randy Armstrong
Admin
Forum Posts: 1663
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
2
02/10/2021 - 18:42
sp_Permalink sp_Print sp_EditHistory

BAD is intended to indicate the reason for no data and it does not have to be related to a communication problem.

The specification explicitly requires that the value be set to NULL if the Quality code is bad.

If the value is NULL then there can be no value change until the Quality changes to Good or Uncertain.

That said the default behavior is to report changes on a change to Quality as well as value so an update should be reported if the BAD Quality changes to another BAD Quality code. Changes to the timestamp do not trigger a change.

Avatar
Murali Janakiraman
New Member
Members
Forum Posts: 2
Member Since:
10/22/2020
sp_UserOfflineSmall Offline
3
02/11/2021 - 10:27
sp_Permalink sp_Print

Hi Randy, 

Thanks for your response and update on the specification. It seems like when the Quality is Bad, one can use the sub code of LAST_KNOWN_VALUE. When this is set, then we should be able to send values with a BAD quality code right?

Thanks for your clarification,

Murali

Avatar
Randy Armstrong
Admin
Forum Posts: 1663
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
4
02/11/2021 - 18:24
sp_Permalink sp_Print

It seems like when the Quality is Bad, one can use the sub code of LAST_KNOWN_VALUE.

No you can't. BAD quality means the value cannot be used. So there is never a value.

Originally, this was not enforced but too many clients ignored the BAD code and used a bad value so the compliance tests were changed to force Servers to implement it correctly.

You need to use UNCERTAIN quality with the sub code of LAST_KNOWN_VALUE.

Avatar
Zbynek Zahradnik
Member
Members
Forum Posts: 62
Member Since:
02/24/2014
sp_UserOfflineSmall Offline
5
02/12/2021 - 00:10
sp_Permalink sp_Print sp_EditHistory

Randy, there is an exception for Bad quality with LAST_KNOWN_VALUE, quote from the spec:

Last Known Value: "Communications have failed. However, the last known value is available. Note that the ‘age’ of the value may be determined from the TIMESTAMP in the OPCITEMSTATE."

And, LAST_KNOWN_VALUE cannot be used with Uncertain, as you suggested. There is "Last Usable Value" with Uncertain, but that has somewhat different meaning.

 

This said, however, in reality some clients may have problems interpreting the value with Bad/Last Known Value - for the same reason - not following the spec carefully.

Avatar
Randy Armstrong
Admin
Forum Posts: 1663
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
6
02/12/2021 - 01:14
sp_Permalink sp_Print

exception for Bad quality with LAST_KNOWN_VALUE

The OPC UA specification is unequivocal about the no value on BAD quality rule.

COM Clients could suppress the value, even if provided, because of the concern that users would mistakenly assume everything is OK.

The test lab accepts clients that always suppress the value even when it is valid to send a value.

The only requirement is that if the value is displayed the quality but also be displayed.

Avatar
Karl Deiretsbacher
Moderator
Moderators

Moderators-Specifications

Moderators-Companion

Moderators-Implementation

Moderators-Certification

Moderators-ProductsServices

Members
Forum Posts: 12
Member Since:
01/06/2018
sp_UserOfflineSmall Offline
7
02/12/2021 - 04:16
sp_Permalink sp_Print

Please notice the description of "Bad_LastKnown" in OPC UA Part 8:

"OPC UA requires that the Server shall return a Null value when the Severity is Bad. Therefore, the Fieldbus code “Bad_LastKnown” shall be mapped to Uncertain_NoCommunicationLastUsable."

Avatar
Zbynek Zahradnik
Member
Members
Forum Posts: 62
Member Since:
02/24/2014
sp_UserOfflineSmall Offline
8
02/12/2021 - 04:49
sp_Permalink sp_Print sp_EditHistory

Would it be correct to sum it up roughly like this?

"In OPC DA, you can transfer a meaningful value with Bad quality and "Last Known Value" substatus. It may not be a good idea, though, due to unreliable support by real-world clients. When such data enters the OPC UA world, in compliant systems the value will be cleared and thus lost."

Or, should the Part 8 reference to "Fieldbus code Bad_LastKnown" interpreted to apply also to mapping from OPC DA to OPC UA, and therefore the expected outcome is  Uncertain_NoCommunicationLastUsable with the actual value?

Avatar
Randy Armstrong
Admin
Forum Posts: 1663
Member Since:
05/30/2017
sp_UserOfflineSmall Offline
9
02/12/2021 - 05:29
sp_Permalink sp_Print

The mapping for COM DA LAST_KNOWN_VALUE is defined to be Bad_OutOfService:

https://reference.opcfoundatio.....2/#A.3.2.3

Avatar
Zbynek Zahradnik
Member
Members
Forum Posts: 62
Member Since:
02/24/2014
sp_UserOfflineSmall Offline
10
02/12/2021 - 05:36
sp_Permalink sp_Print

Thanks Randy. 

Forum Timezone: America/Phoenix
Most Users Ever Online: 510
Currently Online:
Guest(s) 41
Currently Browsing this Page:
1 Guest(s)
Top Posters:
Forum Stats:
Groups: 2
Forums: 10
Topics: 1512
Posts: 5119